Post by Richard 1774 on Feb 7, 2014 13:05:10 GMT -5
Hi just moved into a new house and the boiler keeps locking out with the error A02. But this resets and it will be ok for a few days and then it will do it again. Does anybody have any ideas as the manual just says press the reset. I am an automotive engineer so more than able to replace parts so any help would be great.
|
|
|
Post by Mike the Boilerman on Feb 8, 2014 6:55:01 GMT -5
Interesting. None of my manuals shows A02 as an error. Does yours? What does it say the fault is? (Other than the need to press 'reset')?
Mike
|
|
|
Post by richard1774 on Feb 8, 2014 12:46:36 GMT -5
Hi A02 just says "system response fault. Open rad valves and reset. If persists call a engineer". This only comes up now an again and only at the start of the cycle. We had a potterton engineer here to carry out a recall on the flue and he said its probably the igniter but to replace the whole igniter system not just the prob. I am not sure because as soon as you reset it lights straight away. Any advise would be great because we both know it isn't going to get any better.
thanks
|
|
|
Post by Mike the Boilerman on Mar 7, 2014 7:02:50 GMT -5
Replacing the control board seems to fix most intermittent problems like this on a Powermax HE. Expensive though, and a risk as it my not fix it!
I'd consider changing it for a better designed boiler if I were you actually. All Powermax models are prone to repeated expensive failures.
Mike
|
|