Post by Women in need of some help?? on Oct 16, 2013 8:49:00 GMT -5
Hi there,
Please can someone help?
I have a powermax 155X boiler and there seems to be a problem with the Hot water.
My hotwater is set to HW Cont but it only seem to have hot water when i press the advance button so both Red Lights are on but as soon as i turn the tap off the hot water stops working and the green light goes off. i then have to wait 10/15 minutes and do the process again.
Can you advise what i need to do?
Thanks
|
|
|
Post by northpole on Nov 12, 2013 8:35:29 GMT -5
The green light will only come on when the burner is operating, which it will do if the hot water temperature in the boiler's internal tank falls below a set value (normally 80 degrees C). If you have hot water set to continuous, you will probably be able to run quite a bit of hot water before the burners need to come on to bring the internal tank temperature up again - it doesn't come on every time you run hot water, as it does with a combi boiler.
The red lights indicate when the programmer is 'on' in accordance with the on/off times which have been set by the user (separately for hot water and central heating) - but if the hot water is set for continuous (top position on the three-way switch), the programmer is by-passed (and you won't get any central heating!).
Does that help at all? Have you looked at the User Manual? - you can download a copy from Mike's site (http://www.powermax-repairs.co.uk/Powermax%20user%20instructions.pdf)
|
|