Post by aviator on Feb 14, 2014 0:23:14 GMT -5
When running the hot water it is never hot enough whereas your site suggests the reverse should be true.
Is there any relationship between the hot water cylinder and the central heating system? I.e. If the heating is on should it affect the hot water ?
Thanks
|
|
|
Post by Mike the Boilerman on Mar 7, 2014 6:58:17 GMT -5
Yes. The Powermax is a thermal store. This means it is full of hot radiator water, A coil of pipe is immersed inside carrying tap water. It enters the coil cold and comes out hot. The blender adds some cold if it is TOO hot.
When this pipe gets restricted badly with water scale, the water comes out hot but very slowly. The belnder has to hold back the cold pressure to prevent mixing occurring but eventually succumbs and lets cold water past. This results in higher flwo rate at cooler temperature. Your Powermax needs a descale and new blender valve.
Mike
|
|